TOPIC: 3 phase to 1 phase

3 phase to 1 phase 08 Jul 2018 17:39 #99700

  • Bob Marsland
  • Bob Marsland's Avatar Topic Author
  • Offline
  • Posts: 1706

Derek and Janice Wallace wrote: Be sure to use only the same phase throughout the boat. If you use different phases you have a potential 415v risk.

Derek


Thank you for your cautionary point, Derek. Since I intend to use this as my shore power there will be no other source of 230v alive at the same time. If the shore power trips and I resume to inverter power/ generator there still will not be a conflict as the single phase out of three has tripped. My MasterVolt Masterswitch allows only one source of electrical power at any given time.

Bob

Please Log in to join the conversation.

Bob & Bobbie Marsland
MS La Chouette

3 phase to 1 phase 08 Jul 2018 15:32 #99699

  • Derek and Janice Wallace
  • Derek and Janice Wallace's Avatar
  • Offline
  • Posts: 166
Be sure to use only the same phase throughout the boat. If you use different phases you have a potential 415v risk.

Derek

Please Log in to join the conversation.

3 phase to 1 phase 08 Jul 2018 11:25 #99695

Apologies to Dave Targett, this post was actually from Chris Grant but I was testing Dave's membership login which had been causing him trouble.
The following user(s) said Thank You: Bob Marsland

Please Log in to join the conversation.

3 phase to 1 phase 08 Jul 2018 11:15 #99694

Absolutely no reason not to Bob. Neutral to phase is 230V and phase to pahase 400V in Europe.

Bob Marsland wrote: Is there any reason I cannot/should not wire a five pin three phase plug to a regular 16 amp 230v socket just using one of the live phases, the neutral and the earth?
Bob

The following user(s) said Thank You: Bob Marsland

Please Log in to join the conversation.

3 phase to 1 phase 08 Jul 2018 10:57 #99692

  • Bob Marsland
  • Bob Marsland's Avatar Topic Author
  • Offline
  • Posts: 1706
Is there any reason I cannot/should not wire a five pin three phase plug to a regular 16 amp 230v socket just using one of the live phases, the neutral and the earth?
Bob

Please Log in to join the conversation.

Bob & Bobbie Marsland
MS La Chouette